Re: Generator inlet receptacle installation on house
Posted: Thu Dec 24, 2020 2:33 pm
So for future reference I just took a few current measurements in my panel.
Oven preheating. About 12.5A on one line and 20.3A on the other line. My generator is rated for a max of 16.66A per line, steady state. I'm sure it could surge up to 20A and a little beyond (it has 20A breakers, and the breaker feeding the panel is 20A so anything over 20A is going to become breaker limited, for safety). So realistically, I could not preheat my oven even if I turned everything else off. My assessment is it would be pegging one line at 20A for several minutes on end and that's just a bit too far over the limit.
However, once the oven is preheated, the element duty cycle is pretty low and only rises to ~12.xA per line, with a brief spike to 17A that would probably be tolerable provided little else was running at the time. Now for more relevant news (because it's not worth attempting oven use....). My microwave draws more current than I expected, which explains why it seems to hard on the generator. That's because it pretty much pegs one line when it's running. Sigh. Microwaves are so inefficient. In the future I will have to pretty much make sure all loads on that line are off when running the microwave.
This is a good example of why you can't just add up watts of loads. Is it a 240V load? 120V? If 120V, which line (1 or 2)? Not to mention, the microwave is probably rated at 1000 or 1100 but that's cooking power I guess. It's actually drawing like 1950W. Again my gen is 4000W but that's nominally 2000W per line. So you can see why I say it would peg one line. Because that's exactly what it is doing.
Oven preheating. About 12.5A on one line and 20.3A on the other line. My generator is rated for a max of 16.66A per line, steady state. I'm sure it could surge up to 20A and a little beyond (it has 20A breakers, and the breaker feeding the panel is 20A so anything over 20A is going to become breaker limited, for safety). So realistically, I could not preheat my oven even if I turned everything else off. My assessment is it would be pegging one line at 20A for several minutes on end and that's just a bit too far over the limit.
However, once the oven is preheated, the element duty cycle is pretty low and only rises to ~12.xA per line, with a brief spike to 17A that would probably be tolerable provided little else was running at the time. Now for more relevant news (because it's not worth attempting oven use....). My microwave draws more current than I expected, which explains why it seems to hard on the generator. That's because it pretty much pegs one line when it's running. Sigh. Microwaves are so inefficient. In the future I will have to pretty much make sure all loads on that line are off when running the microwave.
This is a good example of why you can't just add up watts of loads. Is it a 240V load? 120V? If 120V, which line (1 or 2)? Not to mention, the microwave is probably rated at 1000 or 1100 but that's cooking power I guess. It's actually drawing like 1950W. Again my gen is 4000W but that's nominally 2000W per line. So you can see why I say it would peg one line. Because that's exactly what it is doing.