Hot water heater issues
Posted: Sat Nov 21, 2015 4:08 pm
Over a period of several months, we'd lose hot water and the fix was to press the reset switch on the oil burner. This would happen as frequently as once a week or go a much longer period. Today it happened repeatedly - it wouldn't even light off.
I guess I figured out what that circuit is doing. When the thermostat calls for heat, the burner fires up. First the fan, then the igniter (like a spark plug) and then oil injection (the fan and oil injection may happen at the same time). In this case, I could hear that there was no flame. It was just injecting oil into the firebox. Great. So when I reset it, it would try to run and after 5 seconds or so of no flame, it would shut itself down.
I almost gave up right there and called for service, as I think it is due anyway.
But I got bold and decided to open up the transformer assembly. Just loosen these two screws and the retainer plates swing out of the way. The transformer is on a hinge, and this is the label plate. Yes, 10,000 VDC. So this is pretty simple. Those springs make contact on the rods and that carries the voltage/current to the igniter which is probably pretty close to the injector. Think of it like a flame thrower. I took some sandpaper and sanded both the springs and the rods, which you can see here: I put it all back together and it fired right up.
I will definitely be keeping my eye on it as there could be other reasons the flame doesn't ignite (the transformer itself and the control circuitry mainly).
At least this is all based on my understanding of how it works. I guess I could go look it up online, but that's boring.
By the way, this is only a 30 gallon tank and I basically have unlimited hot water. The burner capacity on this, compared to a gas unit, is considerably higher. It's got enough capacity that, during a shower, it will kick on, get the water back up to 130°F and actually shut off again. DURING a shower.
The rating is 118 GPH (gallons per hour) at 100°F temperature rise. So if the water coming out of my well was 45°F, it could make 145°F water at a rate of 2 gallons per minute. Since it only needs an 85°F rise, I'd estimate 2.35 GPM, continuous. My shower head is rated at 2.0 GPM max (I think at 80 psi). My well water pressure never gets that high, so figure 1.75 GPM. 1.75 / 2.35 ~= 75% duty cycle (6 minutes on, 2 minutes off, etc.). So there's the math on why the hot water heater can actually cycle during a shower. Yay.
I guess I figured out what that circuit is doing. When the thermostat calls for heat, the burner fires up. First the fan, then the igniter (like a spark plug) and then oil injection (the fan and oil injection may happen at the same time). In this case, I could hear that there was no flame. It was just injecting oil into the firebox. Great. So when I reset it, it would try to run and after 5 seconds or so of no flame, it would shut itself down.
I almost gave up right there and called for service, as I think it is due anyway.
But I got bold and decided to open up the transformer assembly. Just loosen these two screws and the retainer plates swing out of the way. The transformer is on a hinge, and this is the label plate. Yes, 10,000 VDC. So this is pretty simple. Those springs make contact on the rods and that carries the voltage/current to the igniter which is probably pretty close to the injector. Think of it like a flame thrower. I took some sandpaper and sanded both the springs and the rods, which you can see here: I put it all back together and it fired right up.
I will definitely be keeping my eye on it as there could be other reasons the flame doesn't ignite (the transformer itself and the control circuitry mainly).
At least this is all based on my understanding of how it works. I guess I could go look it up online, but that's boring.
By the way, this is only a 30 gallon tank and I basically have unlimited hot water. The burner capacity on this, compared to a gas unit, is considerably higher. It's got enough capacity that, during a shower, it will kick on, get the water back up to 130°F and actually shut off again. DURING a shower.
The rating is 118 GPH (gallons per hour) at 100°F temperature rise. So if the water coming out of my well was 45°F, it could make 145°F water at a rate of 2 gallons per minute. Since it only needs an 85°F rise, I'd estimate 2.35 GPM, continuous. My shower head is rated at 2.0 GPM max (I think at 80 psi). My well water pressure never gets that high, so figure 1.75 GPM. 1.75 / 2.35 ~= 75% duty cycle (6 minutes on, 2 minutes off, etc.). So there's the math on why the hot water heater can actually cycle during a shower. Yay.